Can the onboard capacitors on the Jetson AGX Orin DevKit carrier board provide sufficient hold-up time for the Orin module to finish a graceful shutdo
Hi,Can the capacitors on the Jetson AGX Orin DevKit carrier board provide sufficient hold-up time for the Orin module to finish a graceful shutdown upon sudden loss of external power? Can we optimize the shutdown sequence in software to shorten shutdown duration? What is the minimum latency from shutdown signal reception to power-off on the Orin module? Thanks.
The Dev Kit carrier has a power loss detection circuit that sets the VDDIN_PWR_BAD_N input to the module low ~6.25-6.5V to trigger the on-module power sequencer to immediately start an emergency hardware shutdown, so it would try to follow a “graceful” shutdown from a hardware power sequencing point of view but it likely would not be a graceful shutdown software-wise. There is some applicable discussion for AGX Orin on this topic at Sudden Power Loss AGX Orin
So my understanding is as follows: The assertion of VDDIN_PWR_BAD_N triggers the hardware-initiated shutdown sequence rather than a software graceful shutdown. If we want to execute a software graceful shutdown, we need an additional power-loss detection circuit configured with a higher voltage threshold. Once this higher threshold is crossed, the system shall start the software shutdown procedure. Is this understanding correct?Thanks.
The software graceful shutdown time can vary depending on your use case and the type of storage you use.
If you need more time for the SW graceful shutdown, you can add extra capacitors (though this approach has limitations due to physical space constraints and added cost, and it may not increase the hold-up time significantly). Also, as you mentioned, raising the voltage monitoring threshold is a valid option.
However, please keep in mind that doing this can make the system detect low voltages more easily, which might cause the system to shut down more frequently."